w_tom wrote:
> On Feb 10, 4:56 pm, Dudley Henriques <dhenriq....RemoveThis@rcn.com> wrote:
>> I just want to thank everyone who answered in this thread. I read all of
>> it and appreciate your time. I learned a lot from your input.
>
The best information on surges and surge protection I have seen is at:
http://omegaps.com/Lightning%20Guide_FINALpublishedversion_May051.pdf
- "How to protect your house and its contents from lightning: IEEE guide
for surge protection of equipment connected to AC power and
communication circuits" published by the IEEE in 2005 (the IEEE is the
dominant organization of electrical and electronic engineers in the US).
And also:
http://www.nist.gov/public_affairs/practiceguides/surgesfnl.pdf
- "NIST recommended practice guide: Surges Happen!: how to protect the
appliances in your home" published by the US National Institute of
Standards and Technology in 2001
The IEEE guide is aimed at those with some technical background. The
NIST guide is aimed at the unwashed masses.
>
> Read numeric specs for a UPS. Where are numeric claims for hardware
> protection? It does not. Why does the manufacturer not even claim
> what others have posted here?
Contrary to w_’s beliefs, both the IEEE and NIST guides say plug-in
suppressors are effective. Ratings range from junk to very high. The
same protection can be built into UPSs. Any surge suppressor in the US
should have a UL1449 listing.
>
> Second, why would a UPS protect Ethernet ports?
All interconnected equipment needs to be connected to the same plug-in
suppressor, or interconnecting wires need to go through the suppressor.
External connections, like ethernet, phone, also need to go through the
suppressor. Connecting all wiring through the suppressor prevents
damaging voltages between power and signal wires. These multiport
suppressors are described in both guides.
According to NIST guide, US insurance information indicates equipment
most frequently damaged by lightning is
computers with a modem connection
TVs, VCRs and similar equipment (presumably with cable TV
connections).
All can be damaged by high voltages between power and signal wires.
> Protection is defined by earth ground. A protector with
> that short (less than 10 foot) connection to earth has THE only
> required component in every protection solution: earth ground.
w_ has a religious belief (immune from challenge) that surge protection
must use earthing. Thus in his view plug-in suppressors & UPSs (which
are not well earthed) can not possibly work. The IEEE guide explains
plug-in suppressors work by CLAMPING the voltage on all wires (signal
and power) to the common ground at the suppressor. Plug-in suppressors
do not work primarily by earthing. The guide explains earthing occurs
elsewhere. (Read the guide starting pdf page 40).
>
> Every wire in every cable (including underground cables - see that
> figure) makes a short connection to single point earth ground where
> the cable enters a building. A 'whole house' protector in a breaker
> box can do just that.
A service panel suppressor is a good idea.
For best protection, the phone, cable, ... entry protectors need to be
connected with a *short* wire to the earthing wire *at the power
service*. When a strong surge is earthed, the 'ground' voltage in the
house can rise thousands of volts above 'absolute ground'. The goal is
to minimize the voltage between signal and power ground references. The
effect of a ‘ground’ wire that is too long is illustrated in the IEEE
guide starting pdf page 40.
> TV
> (coax) cable drops down to make an earthing connection before entering
> the building.
Commenting on cable entry ground blocks, the IEEE guide says “there is
no requirement to limit the voltage developed between the core and the
sheath. .... The only voltage limit is the breakdown of the F
connectors, typically ~2–4 kV.” And "there is obviously the possibility
of damage to TV tuners and cable modems from the very high voltages that
can be developed, especially from nearby lightning."
========================
The Pournelle Byte article that Howard referred to is at
http://www.jerrypournelle.com/computing/august89.html
A 16,000V power line dropped on the 120V line to his house. Surge
suppressors (plug-in or service panel) are not made for the long
duration of such an event. The author of the NIST guide has said "in
fact, the major cause of TVSS [surge suppressor] failures is a temporary
overvoltage, rather than an unusually large surge."
Pournelle had a computer on a UPS that continued to function through
the event (how did that happen w_?)
The IEEE guide describes at length that in a plug-in suppressor the
protected load can be connected across the MOVs or connected ahead of
them. If the protected load is connected across the MOVs, it will be
disconnected when the MOVs are disconnected on failure (as now required
by UL). A few plug-in suppressors disconnect on overvoltage. A UPS may
switch to battery on overvoltage.
--
bud--
>> Stay informed about: House Power Failures and Mac